wetlook wrote: Tue Apr 30, 2024 8:42 pm
This is a cobbled together system in an early Mustang.
Which model year is this Mustang? I presume you've charged it with R-134a. Do you have the original R-12 specs for this car as a baseline?
wetlook wrote: Tue Apr 30, 2024 8:42 pm
When first started at idle, the pressures settle to 25/150 on a 70F day and it blows 44ish out the vents. As soon as I raise the rpm above idle, the pressures go to 10/250-275 and the vent temp climbs.
At idle, the pressures both seem low at that ambient temperature, but normal RPM for testing purposes is around 1,800, as you mentioned below. So the pressure readings at idle don't tell us much because the compressor isn't doing much. However, with the engine running above idle (~1,800 RPM), the low pressure is still too low and the high pressure is still too high.
wetlook wrote: Tue Apr 30, 2024 8:42 pm
If left to idle after being at 1800rpm the high side stays over 200 for quite some time.
It definitely has a low charge, but I suspect any more refrigerant would shoot the high side to the moon.
I forgot to look at the equalization time when shut off.
Feeling the in/outlets by hand, the condenser is doing a good job.
I'm thinking the old TXV is not working properly, that that seem reasonable?
When shut down, some systems take more time to equalize their pressures than others.
How do you know that it's low on refrigerant? Did you charge it
by weight using an accurate refrigerant scale (not the sight glass) equaling the original R-12 specification, or a bit less? How much oil did you put in it? Did you thoroughly flush the evaporator to get rid of all the mineral oil left over from the car's R-12 days?
With a low-side pressure at only 10 PSI, it's possible that the TXV is defective, as you suggest, or that it's partially clogged by debris.
wetlook wrote: Tue Apr 30, 2024 8:42 pm
Although there's a bit of a story regarding the guy who made the hoses......
Apparent he did half and returned a week later because he didn't have the correct fittings on hand. During this time he apparently left the drier open...
I know it needs replacement because of this, but could a moisture saturated dryer cause enough restriction to cause these symptoms?
The desiccant could be full of moisture, especially if it's the original R/D. It could also have some kind of debris in there that's partially blocking the internal screen.
wetlook wrote: Tue Apr 30, 2024 8:42 pm
I could not feel a temperature drop across the dryer, but am unsure if that's a valid test.
It is a valid test, but you'd have to gauge the temperature on each side using the proper equipment, not necessarily by feel. If the R/D is partially plugged, you would be able to measure a temperature drop between the inlet of the R/D and the outlet.
On the TXV, does the equalization line and/or the sensor line look damaged? If so, definitely replace it, even if you haven't examined it internally yet. And, of course, replace the R/D now, and each time the system is opened to the atmosphere.